The NEC is full of ?double-speak,? and is often hard to follow. I agree with Physis. Here is my reasoning process:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">220.16(B) says to include 1500 VA for the laundry branch circuit as required by 210.11(C)(2).</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">210.11(C)(2) says to install at least one branch circuit to serve the laundry outlet that is required by 210.52(F).</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The two exceptions to 210.52(F) give situations in which a laundry outlet is not required.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">If you don?t need the outlet, then you don?t need the branch circuit.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">If you don?t need the branch circuit, then you don?t need to include the 1500 VA.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">QED