No exception in the '08 Code.
There was an exception in earlier Codes.
 
Can someone clear this up for me?

In an unfinished basement, is there any exception that allows a single receptacle for a washing machine to not be GFCI protected?

Rec't is less than 7' high.
It is an independent circuit.

thanks in advance
No, not under the 08 code.
 
Article 210.8(5) calls for GFI protection in unfinished basements. Under the 05 there is an exception that your install may meet. Under the 08 this exception has been removed.
 
Can someone clear this up for me?

In an unfinished basement, is there any exception that allows a single receptacle for a washing machine to not be GFCI protected?

Rec't is less than 7' high.
It is an independent circuit.

thanks in advance

If you jump the border to NJ there might be.
:)
 