Lay factor Medium Voltage Cable
Hello,
I am trying to calculate the resistance of a concentric neutral with a helically configuration for a medium voltage conductor with copper wires.
However, I can not find a correct formula to calculate the "lay factor."
I wonder if some of you have made this calculation before and could help me?, I do not understand the manufacturer's explanation.
The cable is a #1/0 AWG, EPR, 34.kV, CU
Attached is my spreadsheet, also is attached the explanation of the manufacturer for the lay factor calculation.
Regards,
  • HELICALLY NC.xls
  • Lay factor-min.pdf
At first the article Helically Applied Cu Wire CN it is for shield only and not for conductors.
From Lay Direction and Length:
m=1.0619541
UL 1072/1995 7 Resistance
7.1 The direct-current resistance of any length of conductor in ohms per thousand conductor feet or in ohms per conductor kilometer shall not be higher than the maximum acceptable (nominal x 1.02) resistance indicated in Tables 7.1 - 7.10 at 20°C (68°F) or at 25°C (77°F). If, as provided for in 9.2, metal-coated wires are used in only the outer layer of an uncoated copper conductor, the direct-current resistance of the wires are used in only the outer layer of an uncoated copper conductor, the direct-current resistance of the construction.
If you are a customer the maximum resistance at 20oC of the copper conductor has to be 0.102*1.02=0.10404 ohm/kft
If you are a manufacturer the maximum resistance at 20oC of a copper strand before stranding has to be 0.102*1.02/1.0619541*19=1.861436 ohm/kft
Then after stranding conductor resistance will be : 1.861436/19*1.0619541=0.10404 ohm/kft.
I am sorry I did not remark you intend to calculate the resistance of a concentric neutral with a helically configuration and not the conductors. Let's start from the beginning.:ashamed1:
Hello,
Thanks for your answer,
Area you sure about this?': At first the article Helically Applied Cu Wire CN it is for shield only and not for conductors.?
m=1.0619541
I think the problem is the lay factor. In order to calculate the concentric wire resistance you need to know the actual wire length for a foot length of the cable.
The lay factor then will be m=wirelength/laylength
wirelength=√[Laylength^2+(πDinscore)^2]
m=√[1+(πDinscore)^2/Laylength^2]
laylength=no*Dinscore
where Dinscore it is the cable insulation core[here approx.1.13 inch including half of the nonmetallic insulation shield]
no=8_16 ; I think no=12 is good.
tan(a)=laylength/πDinscore ; tan(a)=no/π ; a=atan(no/ π)
If no=12 a=75.3 degrees.
m=sqrt(1+(pi()/12)^2)=1.0337