Layout help
Kevin.hndz
New york
Please help with laying out when dimensions aren't present only info is the 2' to the center of lights everything else is just equal space throughout. How do I get these measurements
busman
Northern Virginia
Master Electrician / Electrical Engineer
In algebra terms, if L is the length of the room and N is the number of fixtures and D is the distance from wall to first fixture, then it is:
Spacing = (L - (2 * D)) / (N - 1)
In an example if the L is 24', N is 3 and D is 2', then (24 - 4) / 2 = 10'
infinity
New Jersey
Journeyman Electrician
There is one dimension missing. For the spacing going north and south you measure the length of the wall to the left or right, come in 2' from each end and then using the remaining measurement to go equal/equal. So for example if the wall is 20' then 20'-4'=16' 16'/2 = 8' apart.
The east to west dimension off the wall is not given so you cannot determine the spacing.
Kevin.hndz
New york
What if I don't have D because the 2 feet if you notice is not the distance from the wall to the first light but center of the light taken from the outside of the wall
Kevin.hndz
New york
That's what
That's what I'm saying because North and South there is no wall. So if you look at the drawing off to the left, the measurement is from the outside of the wall to the center of the lights so in other words I can do the center of the two outside lights no problem because I know it's 2 ft from the wall. I need help with getting the spacings going east to west
infinity
New Jersey
That's what I was thinking because the rest just says eq throughout the spacings
Designers leave dimensions off of a drawing all of the time so it's not uncommon. You could also measure the actual north/south wall length in the field to make your own scale if the drawing is not drawn to scale.
infinity
New Jersey
T
This still doesn't not give me the measurement off the wall to the first light going east to west
If you use Ron's dimensions you do not need a dimension off of the wall. Start with the light in the center between the two walls and then apply Ron's dimensions.
rambojoe
phoenix az
Wireman
Beat me to it... you can also just do the math on floor.. no need for calculus:)
Floor helps since it looks like you are hanging from the deck. Bosch lasers rule! Id ignore the exit on this print...or page rather..
wwhitney
Berkeley, CA
Retired
I take "EQ" to be the same for both E-W and N-S, so in your example the E-W spacing is also 8' apart. Still unspecified whether the resulting square grid should be centered between the E and W walls, but doing so is likely a safe bet.
Cheers, Wayne
Kevin.hndz
New york
Cheers, Wayne
This still doesn't give me the space off the wall 😫
wwhitney
Berkeley, CA
Retired
Sure it does. If the room is say 22' E-W by 20' N-S, then infinity already explained the light spacing would have to be 8' N-S to comply with the drawing. If you take the spacing to also be 8' E-W, and you want the westmost column the same distance off the west wall as the eastmost column is off the east wall, that distance is 3'. Because 3' + 8' + 8' + 3' = 22'.
Cheers, Wayne
infinity
New Jersey
I wouldn't. The equal/equal dimensions are unique to each direction. Having said that they could be the same if that is what the designer wants but no one should be making an assumption.
Your question has already been answered regarding the "off the wall" dimension.