Layout Question

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Sorry a wiring question. Remember not an electrician so like input from the pro’s.
Not showing verticals in the picture.
MC cable being used.
Separate neutrals.
The square in the middle is 4 11/16” box that a 1” conduit from the panel with 5-1P-20(#10’s) circuits will come to.
I’m assuming a separate 12/2 mc cable for the receptacles for each circuit. So (5) mc cables will hit the box along with the 1”.

Does my layout/wiring make sense?

My concern, which I need to check, is the box size. I may need a bigger box for all (5) circuits. Maybe a 6x6.

Instead of a separate 12/2 mc cable to circuit #8 & 14 receptacles does it make more sense to run a multiple neutral mc cable to the first receptacle(circuit #8) then 12/2 to circuit #14 receptacle? This alternative layout is shown in red.

Thank you.
 

Attachments

  • Screenshot 2023-03-24 084626.jpg
    Screenshot 2023-03-24 084626.jpg
    226.4 KB · Views: 38

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
5 20 amp circuits on a #12 is a potential derating problem and yes, in all likelihood the 4-11/16 is undersized
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I think you are getting way off into the weeds here. This should be left up to the guys doing the wiring. Having said that, I would not want to have to splice ten circuits and EGCs in one jbox unless it was sixteen inches or bigger. Nippling some 4-11 boxes and pulling the home runs into them without splices is another option. Let the guys in the field decide.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I think you are getting way off into the weeds here. This should be left up to the guys doing the wiring. Having said that, I would not want to have to splice ten circuits and EGCs in one jbox unless it was sixteen inches or bigger. Nippling some 4-11 boxes and pulling the home runs into them without splices is another option. Let the guys in the field decide.
5 circuits not 10.
Maybe a bit into the weeds but also want to make sure I’m close on the amount of my cable that’ll be used.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would use 2-wire MC cable as depicted. Also we would never use a single 4 11/16 box with a 1" home run conduit. We would use a 3 or 4 gang rough house box. A 6X6 would also work. Some of our foremen only use 12X12's. Here's our typical home run box.