LB 2 Inch

Status
Not open for further replies.

wirenut46

Member
Location
United States
?I have a 2 inch lb 63 cubic inches diameter. It is on the outside of a house under a disconnect looks like somebody changed the service. It has a piece of SER Cable in it with three 250 kcmils and a ground i need to know how to calculate this its seems to be very small to me. Thanks.:?
 
Last edited:
Most LB's that size have the wire size stamped on it but if the wire is there you won't be able to see it. I think it is 4 --3/o conductors
 
Thank You.

Thank You.

Thanks Dennis you are right i tried to look im going to change it this week two a 2.5 inch... I looked in the 2.5 inch and it stated 300 kcmill... I like the hippy stuff dude i used two own for smoke shops.
 
Conductor fill may be ok but you might want to check the minimum bending radius if it's installed in the form of a jacketed SER cable.
 
Conductor fill may be ok but you might want to check the minimum bending radius if it's installed in the form of a jacketed SER cable.

I agree, in almost every scenario SE cable is an LB conduit body is a violation.
 