LB for utility secondary

Status
Not open for further replies.
I have to install a new 400 amp 3 ph service into an existing electric room, I wanted to build it outside, but the building wont let me. Can I use an LB outside for the utility secondary to go inside the back of the new meter inside or do I have to burrow and chip out the floor and footer? Big difference in my pricing!!
 

mivey

Senior Member
Unless the utility takes issue with the LB or having the meter inside, I don't see a problem.
 

Fulthrotl

~Autocorrect is My Worst Enema.~
I have to install a new 400 amp 3 ph service into an existing electric room, I wanted to build it outside, but the building wont let me. Can I use an LB outside for the utility secondary to go inside the back of the new meter inside or do I have to burrow and chip out the floor and footer? Big difference in my pricing!!

if it's ahead of the meter, many utilities won't permit it.
if there is a way to apply utility seals to it to prohibit access,
they may allow it.


ask before you quote.
 