Lb Under Ground
domnic said:
Can i install a lb under ground ?
You mean in a handhole or direct-buried?
I believe the answer would be yes and no.
I also believe you should ask the maker.
(Of the LB, not the made-everything guy.)
The cover will have to be accesible.
314.29 Boxes, Conduit Bodies, and Handhole Enclosures to Be Accessible.
Boxes, conduit bodies, and handhole enclosures shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.
Exception: Listed boxes and handhole enclosures shall be permitted where covered by gravel, light aggregate, or noncohesive granulated soil if their location is effectively identified and accessible for excavation.