Ok so often cat 5 etc. cabling is allowed, per spec, to run unprotected above concealed ceilings.
Is there anything in the code regarding class 2 cable running "free air"( without conduit) above concealed ceiling?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The wiring methods for Class 2 wiring is shown in 725.130 & 725.133.
 

Phil Timmons

Senior Member
Location
DFW
Occupation
Depends on the pay and the day
Ok so often cat 5 etc. cabling is allowed, per spec, to run unprotected above concealed ceilings.
Is there anything in the code regarding class 2 cable running "free air"( without conduit) above concealed ceiling?
Return Air Duct ("Plenum Rated") -- if the ceiling is the return Air Duct.

So we do not put poisonous wire insulation into the air circulation.

Add edit -- also on its own hangers / supports -- generally NOT the ceiling hanger wire, and NOT laying on the tiles.
 