We have many 5,000 volt vacuum breakers & 480 volt motor controllers (AC 3-phase) with 120 volt AC coils. Occasionally an 120 volt coil will become defective (burn up) and be replaced. The coils are not subjected to under or or over voltage and are installed according to manufacture specifications.
Can a LCR meter with the added ESR feature detect if the coil meets manufacturer spec's? As the coil ages & being in service for a long period of time, can this meter measure the inductance and be compared to the manufacturer data sheet?
I have used a LCR meter to troubleshoot a 480 volt 3 phase 30 hp motor finding an ohm imbalance. My Fluke 87 did not detect any issues nor did megging the motor but my LCR meter did because it can measure ultra low resistance. The motor was replaced and service was restored without any issues.
If a coil is subjected to heat, moisture, etc., can a LCR meter be of value?
Thank you