27hillcrest said:
...what will happen when the generator is running? Will the Geneset be able to handle leading power factor? ...
Mostly depends on the generator capability, real power load, and the pf. It may not. Heavy real loads and leading pf are a stability issue. Light real power loads with a low leading pf are a regulator stability issue.
The cummins article is pretty pesimistic. The Cats I'm dealing with have a lot more capability on the leading side of the curve.
27hillcrest said:
...Does leading power factor increase the kw used and the customer will be paying move than they should? ...
Nope. Kw is real power, such as a motor load - the part going out the shaft, or resistive - electric heat. The pf shows the portion that is reactive - current is 90deg out of phase with the voltage. Reactive load draws current, but is not real power. Picture reactive load as storing energy on part of the cycle and returning the stored energy to the gen on the other part of the cycle.
However, the utility could have charge for low pf. Although they rarely squawk about leading pf. It helps counteract all the rest of their industrial customers with lagging pf.
27hillcrest said:
...They have 2 large UPS system in the site. If memory serves me that they would have line side filter bank that might be adding to the leading power factor?? ...
Yes. Cap banks provide leading vars.
27hillcrest said:
...Any thoughts for course of action?...
Get hold of he generator mfg and get the alternator load curve (alternator capability curve). I've had good luck calling the the generator mfg and asking for it. Put a recorder on the line to see what the load is doing. You need to know the pf and real power. Plot the load on the load curve and see if it is within the stability limits.
If it is - Praise be.
If not, the loss of excitation relay will trip the gen or it will slip poles - bad
Let us know how this one turns out - should be interesting.
carl