Hello, I have an issue at one of the 24/7 plants that has me hesitant to pull the trigger on some calcs. We are seeing upwards of 26-27vac leak voltage to approx 20% of the outputs of 3 cards. All three cards are firing some basic Phoenix wafer thin S/P relays(120vac) located in the same enclosure as the PLC. These relays are in turn operating some basic solenoid valves which only draw .1a.
All 27ea relays have typ 15kohm leak resistors installed. The resistors are 12 yrs old( I was the GF on the original install), and show alot of black discoloring/heat damage. One of the resistors is more than likely completely burned thru, allowing the leak voltage to "hold in" the relay after the output is "off". There are other relays which have signs of resistor failure( "ON"LED is constantly lit), but do not yet remain held in after output is off. All other normal functioning relays that do not have an LED that is always on, have 6-7vac leak voltage.
My question is, will my resistor values change for the outputs that are leaking 26-27vac, or are they leaking 26-27vac because of resistor failures? All A/B docs I have studied calculate leak resistor values based on leakage CURRENT. I just wanted to know if anyone knew of a relationship of calculating resistor values based on leak voltages. I am heading out there on Monday and would need to schedule a shutdown to check amperages, but voltages are easily read with no dramas. Am I approaching this correctly?
Thanks in advance!!
Sparky Mike
All 27ea relays have typ 15kohm leak resistors installed. The resistors are 12 yrs old( I was the GF on the original install), and show alot of black discoloring/heat damage. One of the resistors is more than likely completely burned thru, allowing the leak voltage to "hold in" the relay after the output is "off". There are other relays which have signs of resistor failure( "ON"LED is constantly lit), but do not yet remain held in after output is off. All other normal functioning relays that do not have an LED that is always on, have 6-7vac leak voltage.
My question is, will my resistor values change for the outputs that are leaking 26-27vac, or are they leaking 26-27vac because of resistor failures? All A/B docs I have studied calculate leak resistor values based on leakage CURRENT. I just wanted to know if anyone knew of a relationship of calculating resistor values based on leak voltages. I am heading out there on Monday and would need to schedule a shutdown to check amperages, but voltages are easily read with no dramas. Am I approaching this correctly?
Thanks in advance!!
Sparky Mike