Picture four prime power parallel generators feeding a paralleling switchboard, then that feeding building load. 480/277V. NG bond in switchgear only. Breakers are LSIG. These are not standby generators. There is no utility service present.
There is measured ground leakage current coming from the building load displayed on the load breaker.
Am I correct in thinking that this current will move from the load ground paths, through the system bonding jumper, over to the generator neutrals, and then return to the generators? Or asked another way. Should I see ground leakage current on the generator breakers?