Leakage in underground branch circuit

Mike Harkey

Member
Location
Little Rock, AR
Occupation
EE PE
In a 1200A 3P 120/208V switchboard, with (8) 100A 3P breakers feeding (8) different buildings, with the (8) 1/0 panel feeders underground in galvanized rigid steel conduit. Is there a code requirement, or good practice requirement, for a maximum leakage current in these panel feeder conductors, or a minimum impedance when measured with a 'megger'?
 

Mike Harkey

Member
Location
Little Rock, AR
Occupation
EE PE
What would indicate that there is actually leakage?
There is no indication. What I am looking for is a code standard for what leakage would be acceptable, measured either in amps, or in a megger reading on the insulation.
Are we talking Voltage Drop??
No. voltage drop is not an issue. What I am looking for is a code standard for what leakage would be acceptable, measured either in amps, or in a megger reading on the insulation.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
There is no indication. What I am looking for is a code standard for what leakage would be acceptable, measured either in amps, or in a megger reading on the insulation.

No. voltage drop is not an issue. What I am looking for is a code standard for what leakage would be acceptable, measured either in amps, or in a megger reading on the insulation.
No such animal.
Read Art 90.1
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
When I worked industrial we following this guideline:
A general rule when measuring motor insulation resistance is as follows. 2 megohm or less (bad) 2 to 5 megohm (critical)5 to 10 megohm (suspect) 10 to 50 megohm (good) Above 50 megohm (excellent)

I found comparing readings on a annual basis to be the best guide.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
There is no amount of "leakage" that is acceptable, unless you are measuring it at a few milliamps. Keep in mind things like surge suppressors can introduce leakage current.

I would be looking at megohm readings but some conduits might be dry others full of water and that could affect the insulation test readings.

It would be a judgement call IMO. I don't think there is a number that you can use. Now, IF the wires in the same conduit are radically different, that might be meaningful.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
A lot of leakage current comes from capacitance, insulation/resistance testing will not find this current.
 