I have a customer with approximately 40 older, average quality, MR16 bullet-type lights.


He is wanting to add quite a few lights but the transformers and wiring is about maxed out.


If changing out the lamps to LED is the only option price-wise to accommodate the additional lights, which type bulb, supplier, vendor, etc. would you recommend? Existing bulbs are 20W, 35W, and 50W 36 degree.


Obviously, I am not versed at all with the LED conversion bulbs.


Thanks / Regards,
 
I have a customer with approximately 40 older, average quality, MR16 bullet-type lights.


He is wanting to add quite a few lights but the transformers and wiring is about maxed out.


If changing out the lamps to LED is the only option price-wise to accommodate the additional lights, which type bulb, supplier, vendor, etc. would you recommend? Existing bulbs are 20W, 35W, and 50W 36 degree.


Obviously, I am not versed at all with the LED conversion bulbs.


Thanks / Regards,
But, IMO changing out the lamps will not aid if I understand your question correctly. Unless the lampholder is being replaced with an LED lampholder, or removed altogether, then the fixture must still be calculated at the maximum lamp size allowed in the fixture. This won't help increase the number of lights you can add.
 