LED Corn Cob lamp
nizak
On many occasions I’ve seen where Edison base corn cob style led lamps are used in HID fixtures.
Is this a common practice to use a Mogul adapter and then use the cob in place of a HPS , Metal Halide, or Mercury vapor lamp?
Would voltage output from the ballast need to be checked prior to doing it?
nizak
Remove the ballast from the circuit. Make sure your Lamp is suitable for the voltage applied.
I don't know if it's common to use the reducer, but I know of no restriction. I've used them for different types of lamps.
Thank you. I was under the impression the ballast stayed operational .
kwired
Electron manager
NE Nebraska
EC
See lamp instructions. Most you probably need to bypass the ballast but I think there are some designed to be direct replacements for the original lamp.
ramsy
Roger Ruhle dba NoFixNoPay
LA basin, CA
Service Electrician 2020 NEC
Well, you should have known better!🙂
His question was about the lamp but you have a good point.
Owner provided LED's, ordered online, not likely FCC tested, much less NRTL.
Electronic noise from Amazon junk probably destroyed my photocells.
kwired
Electron manager
NE Nebraska
EC
Most photocells are nothing more than a small heat element with current through it controlled by the cell and a contact on a bimetal spring actuated by the heater. Can't believe harmonics or other high frequency noise on the supply line would effect this very much.
EC - retired
My thoughts were the high initial current of the LEDs were the problem.
LarryFine
Henrico County, VA
Electrical Contractor
The ones I'm familiar with have a light-dependent resistor that operates a circuit that triggers a relay or a triac.
I would think that a relay would handle the load. Maybe have your photocell operate a separate contactor.
kwired
Electron manager
NE Nebraska
EC
That would be an issue with the switch contacts not being suitable for the application if that is what is happening.
Though we've used these on magnetic ballasts for years and they probably are comparable or even worse when it comes to initial current?
ramsy
LA basin, CA
For photocell Nameplates that shows "Electronic Ballast" the Amp rating is much less than Tungsten, or Florescent Ballast.
djuly1j3idynn.cloudfront.net/userfiles/images/inriver/original/134402_ek4000%20series%20instructions.pdf
mikeames
Gaithersburg MD
Teacher - Master Electrician - 2017 NEC
Those must be the slow ones that you wait for with tape over them to test. 😞
Knuckle Dragger
Master Electrician Electrical Contractor 01752
Marlborough, Massachusetts USA
They Make corn cob LED lights with mogul bases