I have a limited info scenario on my hands, and the info has trickled in slowly
About 2 months ago I went to a service call, bad gfci on a deck. There's a landscape lighting transformer plugged in that is powering 10 small LED lights on the posts.
There's also a 120v plug which is activated by the built in timer on the transformer.
The homeowner had a string of Christmas lights plugged in there, strung along the railing.
At the time, the concern was that the Christmas lights weren't working. With the new gfci, the transformer powered up and the string of lights came on.
But last Friday, I was called out because 7 of the deck lights are burned out.
I checked the voltage at 2 of the fixtures, where the wires are soldered in, and it showed 12.7 volts AC.
I thought it strange to have AC voltage for 12v LEDs....maybe, maybe not? The lights don't appear to have any labeling on them.
I was under the impression that these lights stopped working one at a time, and was working under that assumption. I was explaining that it could be cheap components in the light, accumulating heat inside the sealed fixtures, etc
Then the homeowner threw me a curve, and said they all worked fine until I changed the gfci.
They didn't like my reply to that, though... They might have worked fine until the gfci went bad, but how could they work just fine when the transformer wasn't getting power from the receptacle?
So my question(s)
Is there a scenario where a voltage spike could damage the LEDs and gfci, but not damage the transformer?
If an LED is designed for DC voltage, yet is powered by AC voltage, does the voltage range need to be narrower?
I'm supposed to speak with the lighting rep who sold them the fixtures and transformer, but thought I'd get some input here first.
About 2 months ago I went to a service call, bad gfci on a deck. There's a landscape lighting transformer plugged in that is powering 10 small LED lights on the posts.
There's also a 120v plug which is activated by the built in timer on the transformer.
The homeowner had a string of Christmas lights plugged in there, strung along the railing.
At the time, the concern was that the Christmas lights weren't working. With the new gfci, the transformer powered up and the string of lights came on.
But last Friday, I was called out because 7 of the deck lights are burned out.
I checked the voltage at 2 of the fixtures, where the wires are soldered in, and it showed 12.7 volts AC.
I thought it strange to have AC voltage for 12v LEDs....maybe, maybe not? The lights don't appear to have any labeling on them.
I was under the impression that these lights stopped working one at a time, and was working under that assumption. I was explaining that it could be cheap components in the light, accumulating heat inside the sealed fixtures, etc
Then the homeowner threw me a curve, and said they all worked fine until I changed the gfci.
They didn't like my reply to that, though... They might have worked fine until the gfci went bad, but how could they work just fine when the transformer wasn't getting power from the receptacle?
So my question(s)
Is there a scenario where a voltage spike could damage the LEDs and gfci, but not damage the transformer?
If an LED is designed for DC voltage, yet is powered by AC voltage, does the voltage range need to be narrower?
I'm supposed to speak with the lighting rep who sold them the fixtures and transformer, but thought I'd get some input here first.