kinda new with led lighting.... i have a 60x60 led light 36watts 10pcs connected, my question is what would be the total load in kva. thank you
kinda new with led lighting.... i have a 60x60 led light 36watts 10pcs connected, my question is what would be the total load in kva. thank you
I don't know what you mean by "60 x 60." But if one item draws 36 watts and you have 10 of them, then the load is 360 watts, or 0.36 KVA. An LED light is a purely resistive load. So it has a power factor of 1.0. Thus, its value in watts is the same as its value in VA.
He must mean 60cm x 60 cm, or a 2' square troffer. Both of you are both right and wrong.Charlie,
An LED is far from a resistive load. LED fixtures that connect to mains require driver electronics which likely include an input rectifier. The power factor of an LED fixture will depend on the design of that input rectifier.
Many (most) modern LED drivers will be designed for a power factor very close to 1.0, but likely not exactly 1.0.
-Jon