coal mines are starting to install LED fixtures
most are having issues with nuisance tripping on the legally required GFCI circuits (our law, all cord connected lighting must be on GFCI unless hard wired)
the wiring is MSHA approved SO type cable
they want to use plugs but eliminate the GFCI due to having to move the lights as the operation continuously advances
I actually went to few mines and measured the I on the G, it varied from 20-50 mA, so the tripping was valid
is this common with LED/GFCI?