LED Lighting in Class I, Div 2 area

Status
Not open for further replies.

In-spector

Member
Location
New Jersey/Pa
Does a LED lighting fixture rated for installation in a Class I Div 2 area require a conduit seal? I would consider LED lighting not an ignition source as stated in 501.15 (A) (1). Correct?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Section 501.15(A) is for Division 1 and only applies to Division 2 if the luminaire is required to be explosionproof. [See Section 501.15(B)(1)]

You should begin with Section 501.130(B) and review the factory applied labels. They should indicate the luminaire's "T-Code" and whether auxiliary seals are required.

Luminaires have some unique "equipment" rules. Review Sections 500.8 (B) and (C), including the FPN/INs carefully.
 