We have a project with a 50' SJOOW cable running from a power/data supply mounted indoors above a drop ceiling to the fixtures mounted on the exterior facade. Is the contractor allowed to run the SJOOW in a conduit or raceway? I am a lighting rep (Please don't hold that against me) and I know we will run into this problem again.
The inspector is calling the SJOOW a portable cord, so he will not allow it. The cable end in the power/data supply is hardwired and the end into the fixture is a connector. Fixture voltage is 120 and power/data supply, cable, and fixture are UL listed as Class II device if that makes any difference. I am not familiar enough with the NEC to know if this is covered or not. Thanks for the help.
The inspector is calling the SJOOW a portable cord, so he will not allow it. The cable end in the power/data supply is hardwired and the end into the fixture is a connector. Fixture voltage is 120 and power/data supply, cable, and fixture are UL listed as Class II device if that makes any difference. I am not familiar enough with the NEC to know if this is covered or not. Thanks for the help.