Jcdunson
Member
- Location
- Apollo Beach, Florida
- Occupation
- Electrical Contractor
I’ve installed an LED lighting system for a major sports venue and the lighting manufacturer has a major safety issue and they refuse to provide data ie: internal fixture wiring schematic so that a solution can be found. The fixtures mount to a steel structure, are made of aluminum and the fixture to structure mate surface of fixture is painted(don’t know why). I’m recording a potential difference of 120 volts between stainless steel screws on exterior of fixture to steel structure. The manufacturer has installed #14awg bond “stingers” from fixture screw to steel structure in an attempt to “make issue” go away. Have noticed since this was done that insulation on #14awg “stingers” is starting to melt at termination(crimp) points. Insulation of 14awg is THHN. I think manufacturer is using equipment ground/ structure as neutral(current carrying conductor) which is a violation of the NEC and a major safety issue. Comments, thoughts are welcome. Thanks in advance. James D.