Led lights blink off through out the new house.

Status
Not open for further replies.

Mark Toler

Member
Location
Mesquite Tx.
Occupation
Electrical contractor
Metal building with wood frame house inside.
Problem: Led lights blink off through out the house. No dimmers in the house.
Corrective actions: Power company did a read out of voltage all good. We put the house on generator power still blinked. Checked all circuits and joints, replaced the main breaker and panel guts. Installed surge suppressor and lightning arrestor. Drove a second ground rod. Removed ceiling fan remote wireless and installed keyless and led bulb. Changed island lights to incandescent bulbs, they blinked off. Appliances are off, heat pump off.
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
I suggest plugging a light into various receptacles around the house to see if it also blinks off. If it doesn't blink then the problem is likely limited to just the lighting circuits. If it still blinks then the problem may be a common feeder, panel, or with the POCO. Also note whether the light gets brighter at times which would indicate that there's probably a loose neutral in a MWBC, the panel, or service.
Can you describe "blinking off" in more detail, such as the frequency and duration of the blinks, and if they seem periodic or random in nature.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Bad batch of bulbs? I got a box of 4 bulbs from Home Depot and a few months later all of them started flickering when they got warm. I couldn't remember which fixtures got those bulbs, but when I replaced the flickering ones, they were all the same make/model. I still have some old fluorescent twisters that just won't die.

So try a different brand bulb unless you already have a mix.
 

WasGSOHM

Senior Member
Location
Montgomery County MD
Occupation
EE
This could be "The tragedy of the Commons." Each OEM feels entitled to dump whatever incompatible garbage onto the rest of you.

Y'all are going to have to wait until we are all more highly evolved. Don't hold your breath.
 

WasGSOHM

Senior Member
Location
Montgomery County MD
Occupation
EE
It’s not an LED problem alone if the incandescent blink off.
Yeah, that points "upstream" as the first problem to be solved.

Once this is solved other problems having to do with the product [or other things] may become visible. Or not, if you're lucky.

I hate callbacks. They're embarassing and they make me doubt myself.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It’s not an LED problem alone if the incandescent blink off.
Exactly. This kind of blinking (from the little we've been told) is often a result of wind moving the service drop, exposing an intermittent connection, like at the butt splices.

Also, investigate whether the offending lights are on one circuit, or on the same phase. As an experiment, I'd try a pair of lights right at the panel.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I don't just take POCO's word for it. I will have them pull the meter so I can check in there. I've found corroded neutrals there several times. Lineman says everything ok but they rarely check the meter and sometimes just do a visual on the drop. Not that they will/can do any repairs in the meter, but they can certainly open it up and look, and if they see problems, they can either call us or have the customer call. I've had them say "everything is good on our end" and then after I've checked everything on the load side I asked them to look again. Then they will usually check the connections at the tranny and drop. Many times they end up changing the crimps either at the drop or pole and that was the problem all along.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I don't just take POCO's word for it. I will have them pull the meter so I can check in there. I've found corroded neutrals there several times. Lineman says everything ok but they rarely check the meter and sometimes just do a visual on the drop. Not that they will/can do any repairs in the meter, but they can certainly open it up and look, and if they see problems, they can either call us or have the customer call. I've had them say "everything is good on our end" and then after I've checked everything on the load side I asked them to look again. Then they will usually check the connections at the tranny and drop. Many times they end up changing the crimps either at the drop or pole and that was the problem all along.
They're also notorious for not checking voltages under load.
 

WasGSOHM

Senior Member
Location
Montgomery County MD
Occupation
EE
Lineman says everything ok

sometimes just do a visual on the drop.

"everything is good on our end"

they end up changing the crimps either at the drop or pole and that was the problem all along.
I've taken tests where they said "Show your work."

I'd ask these guys to "Show your work", how they concluded the problem wasn't with them.
If you ask them to put their readings [and reasoning] in writing you'll really get their attention.

If they say "we're not authorized to do that" you can ask them if they are expressly forbidden.

They want to put the lid on the can of worms and you want to lift the lid.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Many years ago we wired up a building for the County Sheriff communications tower. Radio load was minimal. Blinking tower lights were not. It was several hundred feet underground to the building plus a short span of POCO overhead to the transformer. We had 5 a volt drop at each blink from one side of the road to the other. I expected some VD but not that much. POCO agreed and we got a larger transformer & overhead.

Proof was all we needed.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
Can you describe "blinking off" in more detail, such as the frequency and duration of the blinks, and if they seem periodic or random in nature.
Exactly. Not enough blinking info.

Are all the lights blinking, or just some?
Does the blinking happen in unison, or some here and some there.

Neutral, possible culprit.
I've seen an overhead drop that was spliced, snd one of the compression butts wasn't tight. Lights blinked in the wind, as Larry said.

But I've had unison blinking in "most" of a house, with underground feed. Turned out somebody didn't tighten a hot lug in a pedestal.
 