I recieved a shipment of 3 "architectural Pendant" LED luminaires yesterday. When I opened the crate and removed the packing material the first thing I noticed right next to the UL label was a marking stating this was an incandescent luminaire. Next I removed the canopy from the mounting bracket and found a 5 conductor cable and another label that stated the following: E1= Blue, E2=Green, + = White, - = Black, Dimming = Red. There were no wiring diagram shipped so i tried looking on the manufacturers website for instructions and found nothing. I called the manufacturer and after waiting for over 2 hours final got an email of the components from which the luminaire was built.
The driver is a Lutron HI-LUME product, so my question is this, it appears the E1 & E2 are the class 2 10% dimming control so is it permissable to use the green conductor of this cable for this connection? I do not believe the exceptions in 250.199 apply. The same cable contains the line voltage conductors in addition to the 2 used for the class 2 control.There also appears to be no equipment ground connection from the canopy to the luminaire. Are any of the above stated issues worth reporting this to UL?
The driver is a Lutron HI-LUME product, so my question is this, it appears the E1 & E2 are the class 2 10% dimming control so is it permissable to use the green conductor of this cable for this connection? I do not believe the exceptions in 250.199 apply. The same cable contains the line voltage conductors in addition to the 2 used for the class 2 control.There also appears to be no equipment ground connection from the canopy to the luminaire. Are any of the above stated issues worth reporting this to UL?