230418-1145 EDT
@jaronbrass:
I have created this new thread because your large plots are too much of a time burden. Such large plots are not needed.
You have a new home where all your LEDs flash in unison. I assume you are supplied by a center tapped utility transformer. less likely two phases of a three phase system. Two phases of a three phase system wound not likely be flashing directly in sync, however, it is possible.
I have tested CREE 9.5 W bulbs several years ago, and they had very good operating characteristics.
I would never trust what a power company tells me, unless I can get beyond low level people.
Since all lights seem to be in unison, and are CREE, I would suspect the most likely problem to be external to your main bus bars that breakers plug onto. This means I suspect problem is before said point.
I would suggest a trouble shooting procedure that first evaluates a single CREE or possibly several in some place where there is known stable power. Then at this location you perform various perturbations on supplied AC sine wave voltages, and then at several AC voltages and various voltages and turn on phase shifts. Also turn off phase shifts if that is how your dimmers work. Do these test over very large ranges to see if anything pecular occurs. This should provide some information if bulbs are a problem.
Assuming that bulbs are not likely the direct cause of the problem, then setup test equipment at the main panel, and proceed with monitoring both line voltage and current at the main panel looking for the problem.
I believe my plots that I previously referenced are in couple hundred thousand byte size..
.
@jaronbrass:
I have created this new thread because your large plots are too much of a time burden. Such large plots are not needed.
You have a new home where all your LEDs flash in unison. I assume you are supplied by a center tapped utility transformer. less likely two phases of a three phase system. Two phases of a three phase system wound not likely be flashing directly in sync, however, it is possible.
I have tested CREE 9.5 W bulbs several years ago, and they had very good operating characteristics.
I would never trust what a power company tells me, unless I can get beyond low level people.
Since all lights seem to be in unison, and are CREE, I would suspect the most likely problem to be external to your main bus bars that breakers plug onto. This means I suspect problem is before said point.
I would suggest a trouble shooting procedure that first evaluates a single CREE or possibly several in some place where there is known stable power. Then at this location you perform various perturbations on supplied AC sine wave voltages, and then at several AC voltages and various voltages and turn on phase shifts. Also turn off phase shifts if that is how your dimmers work. Do these test over very large ranges to see if anything pecular occurs. This should provide some information if bulbs are a problem.
Assuming that bulbs are not likely the direct cause of the problem, then setup test equipment at the main panel, and proceed with monitoring both line voltage and current at the main panel looking for the problem.