If you have duct detectors above hung ceilings where are the remote LED usually mounted? In ceiling? In wall? What wiring used between the duct detector and LED? 2 pair fa cable? Thanks.
 

Attachments

  • Capture.jpg
    Capture.jpg
    22.1 KB · Views: 0

ryant35

Member
Location
Cypress, CA
If you have duct detectors above hung ceilings where are the remote LED usually mounted? In ceiling? In wall? What wiring used between the duct detector and LED? 2 pair fa cable? Thanks.

Usually on the ceiling below the duct smoke. I've seen them on walls and columns as well. Mostly a preference.

Run 1 pair of 2#18 between, FPL or FPLP depending on your ceiling.
 