giovanni0502
Member
- Location
- PA
So I saw some LED ribbon cable yesterday. It comes on a 500’ reel and is cut to length at 1’ intervals. Then an adapter is connected on each end to feed it. The driver comes with a 1’ pigtail for 120v “in” and a 1’ cord with adapter “out” for the 0-10v dc side. Both of these cords are factory wired. The manufacturer, whose name escapes me right now, provides 3’ pre-made jumper cords to go from ribbon to ribbon. It is worth mentioning that this is not a kit per se, but rather a group of components you install separately as a system. The contractor wants to install it as accent lighting above a dropped ceiling, using opaque panels laid in the grid like acoustical tiles to show the light below the ceiling.
Here is my question: the driver and jumpers are all wired with SJEO cord. Now according to article 400, flexible cord isn’t allowed above drop ceilings. Then 2017 NEC 411.5 A 2 makes it appear that it could be if on the load side of a class 2 power supply. I can’t seem to find anything in 725 to allow/not allow flexible cord for class 2 power supplies. Would this installation be allowed above a drop ceiling?
Sent from my iPhone using Tapatalk
Here is my question: the driver and jumpers are all wired with SJEO cord. Now according to article 400, flexible cord isn’t allowed above drop ceilings. Then 2017 NEC 411.5 A 2 makes it appear that it could be if on the load side of a class 2 power supply. I can’t seem to find anything in 725 to allow/not allow flexible cord for class 2 power supplies. Would this installation be allowed above a drop ceiling?