We did a small apartment building next door to the shop a couple years ago.
The owners son lives in one of the units and told us that when he changes the speed via the wall control for the living room fan the LEDs in the Kitchen Dining area blink. Same circuit. It has been doing it for a while but he just got around to telling us. He doesn't change speeds very often so it was not a high priority concern.
The LED lamps that came with the Fan were not affected. Two other mfg of lamps would flicker, a third would not. Incandesents would not.
CH surge suppressor in the panel did no good. The standby snubbers we have on hand worked. The 130 volt reduced the flicker to about once every 15 switch cycles. The 120v removed all flicker. During testing the speed control was in or replaced with a simple switch for testing.
Just something to think about.
The owners son lives in one of the units and told us that when he changes the speed via the wall control for the living room fan the LEDs in the Kitchen Dining area blink. Same circuit. It has been doing it for a while but he just got around to telling us. He doesn't change speeds very often so it was not a high priority concern.
The LED lamps that came with the Fan were not affected. Two other mfg of lamps would flicker, a third would not. Incandesents would not.
CH surge suppressor in the panel did no good. The standby snubbers we have on hand worked. The 130 volt reduced the flicker to about once every 15 switch cycles. The 120v removed all flicker. During testing the speed control was in or replaced with a simple switch for testing.
Just something to think about.