I am working on a rooftop a/c 480 volt 3 phase. Phase to phase is 460. Two of the legs to ground are 277. The other leg reads 12 volts. Is that normal
Agreed. What are you reading line-to-line all the way around?In order.to get 277 to ground it must be a 480Y/277 volt system. I'm thinking blown fuse on one phase.