Leg to ground on 460 3 phase

Status
Not open for further replies.

littlemarine

Member
Location
Pearland Texas
Occupation
A/C technician
I am working on a rooftop a/c 480 volt 3 phase. Phase to phase is 460. Two of the legs to ground are 277. The other leg reads 12 volts. Is that normal
 
Have you measured voltage acroos each fuse (line side to load side) ?
 