Legal or not?
joeboo94
Is it permitted by the code to use NM cable in an industrial building to wire prefabeb offices.
[ December 11, 2003, 11:04 AM: Message edited by: joeboo94 ]
Re: Legal or not?
I have read the articles and it does not really say industrial,what i have going on is they are building four offices,they are used those prefabed panels with the hole through the styrofoam. But it ran in my mind that you couldnt use romex in any industrial application.
[ December 12, 2003, 08:37 AM: Message edited by: joeboo94 ]
Re: Legal or not?
It doesn't boil down to whether the building is industrial, commercial or residential, but rather what types of materials are required to be used to construct the building. Buildings are allowed to be constructed with certain types of materials, depending on the size, height, and use of the building. It also depends on whether or not fire sprinklers are used and fire department access to the building perimeter. That said, it often will happen that industrial occupancies require a very large building, and therefore must be constructed of steel and/or masonry alone. These are type I and II buildings. Section 334.10 does not allow the use of NM in types I and II buildings. This is not to say that if a building is constructed of steel and/or masonry, NM cannot be used, but rather to say that if a building is required to be built with steel or masonry only (type I or II), then NM cannot be used.
What about your building? Did the building official allow the use of wood partition walls? If he did, then NM may be used. If not, then, probably, you may not use NM. See Annex E, for the rules (combustible means wood).