So this is in regard to a previous post about rotary phase converter for some 3/0 cnc machines.
Inspector approved of another feeder to same building serving the phase convert. Since it’s will be for 3phase loads.
That’s complaint since it’s a different voltage.
Though issue I see. If I put the disconnect on the wall I want.
Then one service disconnect would be on wall and the original disconnect would be 20 feet ways on opposite wall.
Inspector did not like that original service disconnect in so far in the building. It’s legal but he likes to make up his own rules.
I called to see what his distance on grouping is. Since both disconnects would be in same room but on directly opposite walls 20 feet as the crow flys.
He avoided answering my question.
Instead he said he fine with the meter outside two now turn into a meter main.
This would make my old feeder non complaint since it is only three wire, and was built after 2008. He said it’s still safer than unfused service conductor that currently are in garage.( they are under concrete so I don’t see his problem).
So since the stipulation for 3wire to building was not prior to 08. Can inspector make his own changes even though it’s black and white???
ABJ has final say on rules that are vague but can he do what he is proposing.
Going to try and pull egc if I can but my be directly buried.
Was going to right in contract but hat Inspetor is allowing this set up??? Any thoughts.
No metallic from service to building. Safety issue is not an issue.
Inspector approved of another feeder to same building serving the phase convert. Since it’s will be for 3phase loads.
That’s complaint since it’s a different voltage.
Though issue I see. If I put the disconnect on the wall I want.
Then one service disconnect would be on wall and the original disconnect would be 20 feet ways on opposite wall.
Inspector did not like that original service disconnect in so far in the building. It’s legal but he likes to make up his own rules.
I called to see what his distance on grouping is. Since both disconnects would be in same room but on directly opposite walls 20 feet as the crow flys.
He avoided answering my question.
Instead he said he fine with the meter outside two now turn into a meter main.
This would make my old feeder non complaint since it is only three wire, and was built after 2008. He said it’s still safer than unfused service conductor that currently are in garage.( they are under concrete so I don’t see his problem).
So since the stipulation for 3wire to building was not prior to 08. Can inspector make his own changes even though it’s black and white???
ABJ has final say on rules that are vague but can he do what he is proposing.
Going to try and pull egc if I can but my be directly buried.
Was going to right in contract but hat Inspetor is allowing this set up??? Any thoughts.
No metallic from service to building. Safety issue is not an issue.