ItsHot said:Legal..define legal!! Is that a sj cord connector on romex?
iwire said:The real volition is using a lighting outlet as a receptacle outlet.
weressl said:More problematic to me is that the device - lampholder - itself is overheated as it is evidenced from the discoloration and on its way to become a firehazard.
whereas said:It is listed as such, but I would be interested in what Code section prohibits the use of such device today.
More problematic to me is that the device - lampholder - itself is overheated as it is evidenced from the discoloration and on its way to become a firehazard.
You volition is to nitpick?![]()
iwire said:410.47 requires that lampholders be installed as lampholders only. A carry over from way back in the day but commonly interpreted as preventing what is shown in the picture.
iwire said:Typically these sockets are only rated 600 watts with 18 AWG conductors, start plugging in other loads and that the current can quickly exceed the lamp holders rating.
iwire said:Perhaps from overload?![]()
iwire said:There is that pot calling the kettle black again. :grin:
weressl said:I agree, but how is the HO to know that when he sees appropriate approval markings on the device?
That of course is not the reasoning why these should not be used, rather the electrocution hazard is given in the handbook.
Receptacle strips have no limitation how much load can be added to them eitehr.
I wonder if there was wattage limitation printed on those old sockets....?
Now it's too late, as we slowly saying goodbye to traditional Edison sockets........
shouldn't be overfilled. Looks like 2 14-2's and a 14-3 for a grand total of 10 conductors times 2 for #14 = 20 cubic inches. I'm pretty sure those 8-b boxes are at least 20 cubic inches right?Jim W in Tampa said:Wonder if it is over on box fill too.