2011 NEC 700.5 (D) states that transfer equipment shall only serve emergency loads. This always seemed logical to me that a legally required generator could only serve EM loads because it is a life safety issue.
However in the handbook right under this article it states that a single generator can serve both EM and non EM loads if seperate transfer switches are used.
So I have two questions. Is the Handbook correct that you can serve both types of loads from a single generator? What is the purpose of seperate transfer switches.
However in the handbook right under this article it states that a single generator can serve both EM and non EM loads if seperate transfer switches are used.
So I have two questions. Is the Handbook correct that you can serve both types of loads from a single generator? What is the purpose of seperate transfer switches.