Hospital has (2) generators (they are not in parallel):
Generator #1 feeds Critical ATS and Life-Safety ATS.
Per NEC, Generator #1 is an emergency generator.
Generator #2 feeds the 3rd ATS. This ATS feeds a panel which has air handler unit
(serving patient rooms and other areas) plus other mechanical equipment
(do not serving patient care areas).
Will generator #2 and third ATS be considered legally required (NEC 701) or
optional standby power system (NEC 702)?
Or this generator is still an emergency generator and the ATS is Equipment branch ATS
belong NEC 517? Thank you.
Generator #1 feeds Critical ATS and Life-Safety ATS.
Per NEC, Generator #1 is an emergency generator.
Generator #2 feeds the 3rd ATS. This ATS feeds a panel which has air handler unit
(serving patient rooms and other areas) plus other mechanical equipment
(do not serving patient care areas).
Will generator #2 and third ATS be considered legally required (NEC 701) or
optional standby power system (NEC 702)?
Or this generator is still an emergency generator and the ATS is Equipment branch ATS
belong NEC 517? Thank you.