In many applications, equipment bonding jumpers must be installed on the outside of metal raceways and enclosures. For example, it would be impractical to install the bonding jumper for a conduit expansion joint on the inside of the conduit. For some metal raceway and rigid conduit systems and conduit systems in hazardous (classified) locations, installing the bonding jumper where it is visible and accessible for inspection and maintenance is desirable. An external bonding jumper has a higher impedance than an internal bonding jumper, but by limiting the length of the bonding jumper to 6 ft and routing it with the raceway, the increase in the impedance of the equipment grounding circuit is insignificant. Exhibit 250.43 illustrates a bonding jumper run outside a length of flexible metal conduit. Because the function of a bonding jumper is readily apparent, color identification is not necessary.