malachi constant
Senior Member
- Location
- Minneapolis
A client had installed a central UPS (80kW, 480 in:208 out) when their facility was built ten years ago. The UPS backs a number of data closets. They called me because batteries have been replaced once and were starting to fail again.
I was surprised to see such a large UPS in a facility of this type and figured the replacement could be downsized. In calling the Client's technology director to confirm he was surprised to learn they even HAD a central UPS, as he had been supplying rack-mounted units for the past ten years. He agreed that him supplying a handful of inexpensive rack-mounted units is preferred to replacing the big boy.
So I need to make a recommendation to the Owner. I am thinking that is to replace the UPS with a step down transformer. But what are the consequences of letting the UPS die a slow death - if we yank out the batteries and just let the internal transformer do its thing? I suppose it could do funny things when the power dipped or went out, maybe there is some way to lock it in the bypass position? I know this is not the perfect world solution, but if I can save them from buying a new transformer since they already have a perfectly good one stored in that UPS...why not?
Any thoughts are appreciated. Thanks!
I was surprised to see such a large UPS in a facility of this type and figured the replacement could be downsized. In calling the Client's technology director to confirm he was surprised to learn they even HAD a central UPS, as he had been supplying rack-mounted units for the past ten years. He agreed that him supplying a handful of inexpensive rack-mounted units is preferred to replacing the big boy.
So I need to make a recommendation to the Owner. I am thinking that is to replace the UPS with a step down transformer. But what are the consequences of letting the UPS die a slow death - if we yank out the batteries and just let the internal transformer do its thing? I suppose it could do funny things when the power dipped or went out, maybe there is some way to lock it in the bypass position? I know this is not the perfect world solution, but if I can save them from buying a new transformer since they already have a perfectly good one stored in that UPS...why not?
Any thoughts are appreciated. Thanks!