Level 1 vs Level 2 NFPA 110 Loads
aelec84
Los Angeles
Electrical Engineer
Hello Forum,
Could you assist in clarifying Section 4.4 of NFPA 110? Is it accurate to interpret that Level 1 systems, as defined by NFPA 110, align with Article 700 loads per NEC, while Level 2 systems per NFPA 110 correspond to Article 701 loads of the NEC?
Thank you.
If you have nfpa link the additional content answers the question.
"The scopes of Articles 700 and 701 correlate well with a Level 1 EPSS and a Level 2 EPSS, respectively."
Optional stand by (702) is not considered in 110.