Customer is buying a "LUCID" EV. They are getting a level 2 charger ( 60 Amp max, iirc). I have no other info on the charger as of now The feed from the panel is going to be EMT with THHN/ THWN condutors in it ( Chicago area, has to be "pipe and wire).
I see that #6 is good to 65 Amp, and the table allows the next standard breaker which would be a 70 (if I need to ). Anyone have a reason that on a 75 foot run I would need to use #4? Last charger I did, was only 25 feet from the panel so no real need to consider voltage drop, and we had the spec sheet.
Any thoughts or ideas???
Howard
I see that #6 is good to 65 Amp, and the table allows the next standard breaker which would be a 70 (if I need to ). Anyone have a reason that on a 75 foot run I would need to use #4? Last charger I did, was only 25 feet from the panel so no real need to consider voltage drop, and we had the spec sheet.
Any thoughts or ideas???