Leviton EV 50 amp receptacle

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
With EV chargers being considered as continuous loads, is it acceptable to use the EV heavy duty receptacle with #6 cu. installed in EMT (not Romex) and use a 2 pole 60 amp breaker? I know the wire is good for it since it's not Romex at 60 C. I'm just not sure about the 50 amp rating of the receptacle on a 60 amp breaker.
 
50A receptacle may not be on a 60A circuit, 210.21(B)(1).

For a 60A branch circuit for a 48A EVSE, you'd need to use a 60A rated receptacle, if they exist and if operating under a version of the NEC for which 625.44 allows it (not 2017 or 2020; didn't check 2023 or 2026 First Draft). Otherwise, hardwire it.

Cheers, Wayne
 
50A receptacle may not be on a 60A circuit, 210.21(B)(1).

For a 60A branch circuit for a 48A EVSE, you'd need to use a 60A rated receptacle, if they exist and if operating under a version of the NEC for which 625.44 allows it (not 2017 or 2020; didn't check 2023 or 2026 First Draft). Otherwise, hardwire it.

Cheers, Wayne

A 60A receptacle is allowed as of 2023.

dd075f8645282037b6372ace32dacf95.jpg
 
50A receptacle may not be on a 60A circuit, 210.21(B)(1).

For a 60A branch circuit for a 48A EVSE, you'd need to use a 60A rated receptacle, if they exist and if operating under a version of the NEC for which 625.44 allows it (not 2017 or 2020; didn't check 2023 or 2026 First Draft). Otherwise, hardwire it.

Cheers, Wayne
nema 14-60 is a thing
 