AL ALIPERTI
Member
- Location
- STAMFORD, CONNECTICUT
LFMC 1 1/2" and larger is interlocked design without an integral bonding wire. When connecting a 480V motor equipment (motor), equipment grounding is achieved through the use of an insulated EGC wire inside the conduit along with the phase conductors. The LFMC is terminated with fittings listed for grounding. NEC 250-100 requires bonding of the raceway itself through means specified in 250.92 (B). However, it the LFMC is not considered continuous how can it be bonded? What happens if there is a wire fault in the 3" LFMC?