LFMC Length

Status
Not open for further replies.

Butler

Member
Is there a max length on Liquidtight Flexible Metal Conduit? LFMC size is 2 inch and conductor voltage is 480VAC.
 
Article 350 does not seem to list any maximum length.

I would point out that an installation longer than 6' requires an EGC be run.
 
Is there a max length on Liquidtight Flexible Metal Conduit?

Don't know how long of a run you're looking at here, but 360 degrees is the max between pull points [350.26]

Don't forget the supporting req's [350.30]
 