B Butler Member Sep 9, 2009 #1 Is there a max length on Liquidtight Flexible Metal Conduit? LFMC size is 2 inch and conductor voltage is 480VAC.
Is there a max length on Liquidtight Flexible Metal Conduit? LFMC size is 2 inch and conductor voltage is 480VAC.
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Sep 9, 2009 #2 Article 350 does not seem to list any maximum length. I would point out that an installation longer than 6' requires an EGC be run.
Article 350 does not seem to list any maximum length. I would point out that an installation longer than 6' requires an EGC be run.
celtic Senior Member Location NJ Sep 9, 2009 #3 Butler said: Is there a max length on Liquidtight Flexible Metal Conduit? Click to expand... Don't know how long of a run you're looking at here, but 360 degrees is the max between pull points [350.26] Don't forget the supporting req's [350.30]