DaveEDesign
Member
I know some one who uses LFNC conduit (because it is easier to cut & handle), but uses this conduit with LFMC fittings (due to sturiness), is this combination not legal as these parts aren't "listed" for use together?
Listed smisted, how about grounding of exposed metal fittings. I have seen people use LFNM with LFMC connectors from a plastic ac disco box over to an ac compressor. The connector at the ac would be bonded, but not the other end of the non mettalic flex conduit. Thats no good. Code.
If you use a LFMC fitting on LFNC and the fitting becomes energized, you would not have a ground fault path to trip the breaker. The fitting would stay energized.