Ref: NEC 230.43
In the wording, LFMC is shown as permissible between raceways or raceway and service equipment. There is no mention of using it between a meter enclosure and service equipment.
Is that Code permissible and, if so, is bonding required.
I see no problem with it and no need for bonding as both enclosures are bonded but with the wording as it is, I feel I may be overlooking something.r
In the wording, LFMC is shown as permissible between raceways or raceway and service equipment. There is no mention of using it between a meter enclosure and service equipment.
Is that Code permissible and, if so, is bonding required.
I see no problem with it and no need for bonding as both enclosures are bonded but with the wording as it is, I feel I may be overlooking something.r