andrew@lgiforensic.com
- White Plains, Ny
I am looking for the limit in length for the use of Liquidtight Flexible Metal Conduit: LFMC. I do not see a limitation in 2014 article 350.12. So is there one?
Hi folks, new here. The confusion over the alleged "six foot rule" drives me crazy. The way I read the code there is no limit to the allowable length of LFMC so long as the total bend does not exceed 360* and the raceway contains an equipment grounding conductor. Does everyone agree (except you NYC guys) ? I'm having an issue with this right now so I'm looking for all the support I can get TIA for your input.
250.118(7) Flexible metallic tubing where the tubing is terminated
in listed fittings and meeting the following conditions:
a. The circuit conductors contained in the tubing are
protected by overcurrent devices rated at 20 amperes
or less.
b. The combined length of flexible metal conduit and
flexible metallic tubing and liquidtight flexible
metal conduit in the same ground-fault current
path does not exceed 1.8 m (6 ft).
This is often a critical issue in hazardous location installations.Flexible Metal Conduit, Liquid-tight (DXHR)
USE AND INSTALLATION
This category covers liquid-tight flexible metal conduit intrade sizes 3/8
to 4 (metric designators 12 to 103) inclusive, forinstallation in accordance
with Article 350 of ANSI/NFPA 70, ‘‘National ElectricalCode’’ (NEC).
Liquid-tight flexible metal conduit is intended for use withconductors in
circuits of 600 V nominal or less. This product may also beused for installation
of conductors in motor circuits, and for electric signs andoutline lighting
in accordance with the NEC.
Liquid-tight flexible metal conduit is sunlight resistantand suitable for use
outdoors.
Where terminated in fittings investigated for grounding andwhere
installed with not more than 6 ft (total length) in anyground-return path,
liquid-tight flexible metal conduit in the 3/8 and 1/2 (12and 16) trade sizes
is suitable for grounding where used on circuits rated 20 Aor less, and the
3/4, 1 and 1-1/4 (21, 27 and 35) trade sizes are suitablefor grounding
where used on circuits rated 60 A or less. See ConduitFittings (DWTT) with
respect to fittings suitable as a grounding means.
The following are not considered tobe suitable as a grounding means:
1. The 1-1/2 (41) and larger tradesizes.
2. The 3/8 and 1/2 (12 and 16) tradesizes where used on circuits rated
higher than 20 A, or where the totallength in the ground-return path is
greater than 6 ft.
3. The 3/4, 1 and 1-1/4 (21, 27 and35) trade sizes where used on circuits
rated higher than 60 A, or where thetotal length in the ground-return
path is greater than 6 ft.
PRODUCT MARKINGS
Liquid-tight flexible metal conduit suitable for directburial is marked
‘‘Direct Burial,’’ ‘‘Burial,’’ ‘‘Dir Burial’’ or ‘‘DirBur.’’
Liquid-tight flexible metal conduit not marked with atemperature designation
or marked ‘‘60 C’’ is intended for use at temperatures notin excess
of 60°C (140°F).
Conduit intended for use in dry or oily locations at atemperature higher
than 60°C (140°F) is marked ‘‘____ C dry, 60 C wet, 70 C oilres’’ (or ‘‘____
C dry, 60 C wet, 70 C oil resistant’’) with ‘‘80’’ or‘‘105’’ inserted as the drylocations
temperature.
Conduit marked ‘‘80 C dry, 60 C wet, 60 C oil res’’ or ‘‘80C dry, 60 C oil
resistant’’ is intended for use at 80°C (176°F) and lowertemperatures in air,
and at 60°C (140°F) and lower temperatures where exposed towater, oil or
coolants.
Conduit that has not been investigated for use where exposedto oil is
marked ‘‘OIL-FREE ENVIRONMENTS ONLY.’’
ADDITIONAL INFORMATION
For additional information, see Electrical Equipment for Usein Ordinary
Locations (AALZ).
REQUIREMENTS
The basic standard used to investigate products in thiscategory is
ANSI/UL 360, ‘‘Liquid-Tight Flexible Metal Conduit.’’
UL MARK
The Listing Mark of UL on the attached tag, the reel or thesmallest unit
container in which the product is packaged, with or withoutthe UL symbol
on the product, is the only method provided by UL toidentify products
manufactured under its Listing and Follow-Up Service. TheListing Mark
for these products includes the UL symbol (as illustrated inthe Introduction
of this Directory) together with the word ‘‘LISTED,’’ acontrol number, and
the product name ‘‘Liquid-Tight Flexible Metal Conduit.’’
UL, in performing its functions in accordance with itsobjectives, does not
assume or undertake to discharge any responsibility of themanufacturer or
any other party. UL shall not incur any obligation orliability for any loss,
expense or damages, including incidental or consequentialdamages, arising
out of or in connection with the use, interpretation of, orreliance upon this
Guide Information.
I would draw attention to the UL White Book which is enforceable through Section 90.3(B):
I might add though, show me the statute that gives an AHJ their "A" and I'll show you in the same statute, or a superior one, where they bear NO responsibility for poor judgement or erroneous approval. It will NOT absolve an owner/employer for any hazards of a noncompliant installation.
As I said in the other thread, I don't know the qualifications of the contactor, engineer or AHJ (inspector); I know mine (and they're pretty good). If not corrected now, "AHJ approval" won't protect your employer from liability should an accident occur. Actually, an accident isn't necessary - an employee complaint is all that's needed and correcting the issue will then be totally on your employer.The contractor says install is correct Art. 501 doesn't say has to be listed, and AHJ can approve. Design engineer still haven't given answer yet, but gave impression he thought was correct. AHJ approved.
But we all know the unlisted material faux LFMC type EF isn't tested for application.
Looks like I did everything I can do pointing this out, hope my company takes my concerns serious enough to get an unbiased second opinion.
Good Ole NEMA Documents.....