LFNC Fittings for DB
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
According to section 356.42 it seems that lfnc connectors, if they are straight not angle ones, are allowed for db. However, I don't see listing on the fitting for DB. The section does not say the fittings must be listed for DB so what's the buzz on this?
356.42 Couplings and Connectors.
Only fittings listed for use with LFNC shall be used. Angle connectors shall not be used for concealed raceway installations. Straight LFNC fittings are permitted for direct burial or encasement in concrete.
I see nothing in the section you've posted that requires the fitting to be listed for direct burial. The fact that it states that listed straight fittings are permitted for direct burial nothing more is required.
I found this in the white book
Liquid-tight Flexible Metal Conduit Fittings — Liquid-tight flexible metal conduit fittings in the 1-1/4 in. and smaller trade sizes are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with the NEC. A straight metallic fitting for use in direct contact with earth is marked ‘‘Direct Burial.’’
Same thing though
Liquid-tight Flexible Nonmetallic Conduit Fittings — Liquid-tight flexible nonmetallic conduit fittings are marked as follows: 1. A fitting for Type A conduit only is marked ‘‘Liquid-Tight Flexible Nonmetallic Conduit Type A Only,’’ ‘‘LFNC-A only’’ or ‘‘FNMC-A only.’’ 2. A metallic fitting for Type B is marked ‘‘Liquid-Tight Flexible Nonmetallic Conduit Type B Only,’’ ‘‘LFNC-B’’ or ‘‘FNMC-B.’’ 3. A nonmetallic fitting for Type B conduit only is marked ‘‘Liquid-Tight Flexible Nonmetallic Conduit Type B Only,’’ ‘‘LFNC-B only’’ or ‘‘FNMC-B only.’’ 4. A nonmetallic fitting for Type C conduit only is marked ‘‘Liquid-Tight Flexible Nonmetallic Conduit Type C Only,’’ ‘‘LFNC-C only’’ or ‘‘FNMC-C only.’’ 5. A straight nonmetallic or metallic fitting for use in direct contact with earth is marked ‘‘Direct Burial.’