LFNC on the ground.

Status
Not open for further replies.

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Can LFNC be laid directly on the ground for 2-3 feet or must it be held up an inch or two so it’s not “laying on the ground”
I saw an installation today where LFNC was connected to a pipe about a foot above grade, then ran 2’ over to a generator.
sort of like this..

5C13F367-1D4D-4F79-9DC7-C0BBC372DB55.jpeg
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There are support requirements for LFNC also there is this which is subjective but IMO this can easily be damaged with a lawn mower.

356.12 Uses Not Permitted. LFNC shall not be used as follows:
(1)Where subject to physical damage
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
There are support requirements for LFNC also there is this which is subjective but IMO this can easily be damaged with a lawn mower.
For arguments sake that piece is 6’ or less…
So just the 356.12?
 