356.30(1) :
(1) Where installed in lengths exceeding 1.8 m (6 ft), theconduit shall be securely fastened at intervals not exceeding
900 mm (3 ft) and within 300 mm (12 in.) on
each side of every outlet box, junction box, cabinet, or
fitting.
Though I always thought 3 feet was the general maximum unsupported distance, this seems to be saying it is 6 feet. That is from 2011 but I think it is the same as 2008 as it was not highlighted as being changed.
One thing to add is just because you are connecting to a motor doesn't necessarily mean flexibility is required. Flexibility for operation and flexibility for connection are not the same thing, you can gain flexibility for connection by removing support methods.