Question if LFNC can be used:
Indoors as an end connection between a PVC conduit run and fixed equipment. This is being done so that the PVC conduit does not have to be bent at funny angles. No flexability required.
Give NEC 2008 356.10 and 12 a good read Uses permitted and not permitted.
356.10 Uses Permitted.
LFNC shall be permitted to be used in exposed or concealed locations for the following purposes:
FPN: Extreme cold may cause some types of nonmetallic conduits to become brittle and therefore more susceptible to damage from physical contact.
(1) Where flexibility is required for installation, operation, or maintenance.