Re: liebert 225kva PDU
For your example question: the answer is yes if all the loads are 1 phase 120V (line to neutral loads).
For the UPS:
On each leg (or phase), you can place 625 amps of line to neutral loads (120V loads). In this case, you would have 625A * 120V * 3 legs = 225KVA.
OR, if your loads are line - line, you will have two loads connected to each line (One from A-B and one from A-C. Same with phases B and C.) In this case, EACH line-line load should draw a maximum of 360 Amps (625/ sqrt(3)). This is because the addition of the current drawn from two loads will be sqrt(3) times the current of each load. The total power drawn could be calculated by: 208V * 625A * sqrt(3) = 225 KVA.
An easier way to understand the total power in this case would be: 208V (across each load) * 360A (the current through each load) * 3 (total number of loads). It is still 225 KVA.
Hope that helps.
Steve