Hello,
In section 9.1.2 of the life safety code (Electrical Systems) there is a mention to section 7.9.2.3 for emergency lighting. Anyone one familiar with this section? I don't quite understand 7.9.2.3(2) and how to incorporate it into the design.
Here is the section
7.9.2.3 The emergency lighting system shall be arranged to provide
the required illumination automatically in the event of any interruption
of normal lighting due to any of the following:
(1) Failure of a public utility or other outside electrical power
supply
(2) Opening of a circuit breaker or fuse
(3) Manual act(s), including accidental opening of a switch controlling
normal lighting facilities.
If I'm providing one circuit to a space coming from an emergency panel, is that not enough?
Thanks.